I'm still in the planning stages of a new kitchen.
There is an existing 32A cooker circuit which at present serves a built in oven. The hob is gas. We plan to replace the oven and move it to another location and replace the gas hob with an induction hob.
The current (pun intended) 32A circuit is on 6mm T&E. What sort of power could I reasonably pull on that cable given that the hob may be around 7Kw, lower powerful ones are available and the oven can be around 4Kw, again lower power models available. Is 11Kw a realistic power draw on 6mm?
I know 10mm would be the preferred option but it would be a royal pita to rewire or add a new circuit.
Thanks for any guidance.